800.133 Installation of Communications Wires, Cables, and Equipment. (A) Separation from Other Conductors. (1) In Raceways, Cable Trays,
Boxes, and Cables. (c) Electric Light, Power, Class 1,
Non–Power-Limited Fire Alarm, and Medium-Power Network-Powered
Broadband Communications Circuits in Raceways, Compartments, and
Boxes.
Communications conductors shall not be placed in any raceway, compartment, outlet box, junction box, or similar fitting with conductors of electric light, power, Class 1, non–power-limited fire alarm, or medium-power network-powered broadband communications circuits.
Exception No. 1: Where all of the conductors of electric light, power, Class 1, non–power-limited fire alarm, and medium-power
network-powered broadband communications circuits are separated from
all of the conductors of communications circuits by a permanent
barrier or listed divider.
Exception No. 2: Power conductors in outlet boxes, junction boxes, or similar fittings or compartments where such conductors are introduced
solely for power supply to communications equipment. The power circuit
conductors shall be routed within the enclosure to maintain a minimum
of 6 mm (0.25 in.) separation from the communications circuit
conductors.
Exception No. 3: As permitted by 620.36.
620.36 Different Systems in One Raceway or Traveling Cable. Optical fiber cables and conductors for operating devices, operation
and motion control, power, signaling, fire alarm, lighting, heating,
and air-conditioning circuits of 600 volts or less shall be permitted
to be run in the same traveling cable or raceway system if all
conductors are insulated for the maximum voltage applied to any
conductor within the cables or raceway system and if all live parts of
the equipment are insulated from ground for this maximum voltage. Such
a traveling cable or raceway shall also be permitted to include
shielded conductors and/or one or more coaxial cables if such
conductors are insulated for the maximum voltage applied to any
conductor within the cable or raceway system. Conductors shall be
permitted to be covered with suitable shielding for telephone, audio,
video, or higher frequency communications circuits.