National Electrical Code 2014
Chapter 8 Communications Systems
Article 800 Communications Circuits
IV. Grounding Methods
800.100 Cable and Primary Protector Grounding.
(B) Electrode. The grounding conductor shall be connected in accordance with 800.100(B)(1), (B)(2), or (B)(3).
(1) In Buildings or Structures with an Intersystem Bonding Termination. If the building or structure served has an intersystem bonding termination as required by 250.94, the grounding conductor shall be connected to the intersystem bonding termination.
(2) In Buildings or Structures with Grounding Means. If the building or structure served has no intersystem bonding termination, the grounding conductor shall be connected to the nearest accessible location on the following:
(1) The building or structure grounding electrode system as covered in 250.50
(2) The grounded interior metal water piping system, within 1.5 m (5 ft) from its point of entrance to the building, as covered in 250.52
(3) The power service accessible means external to enclosures as covered in 250.94
(4) The nonflexible metallic power service raceway
(5) The service equipment enclosure
(6) The grounding electrode conductor or the grounding electrode conductor metal enclosure
(7) The grounding conductor or the grounding electrode of a building or structure disconnecting means that is grounded to an electrode as covered in 250.32(3) In Buildings or Structures Without Intersystem Bonding Termination or Grounding Means. If the building or structure served has no intersystem bonding termination or grounding means, as described in 800.100(B)(2), the grounding conductor shall be connected to either of the following:
(1) To any one of the individual electrodes described in 250.52(A)(1), (A)(2), (A)(3), or (A)(4)
(2) If the building or structure served has no intersystem bonding termination or has no grounding means, as described in 800.100(B)(2) or (B)(3)(1), to any one of the individual electrodes described in 250.52(A)(7), and (A)(8) or to a ground rod or pipe not less than 1.5 m (5 ft) in length and 12.7 mm (1/2 in.) in diameter, driven, where practicable, into permanently damp earth and separated from lightning conductors as covered in 800.53 and at least 1.8 m (6 ft) from electrodes of other systems. Steam or hot water pipes or air terminal conductors (lightning-rod conductors) shall not be employed as electrodes for protectors.
800,100 (B) (1)
Uma terminação de ligação entre sistemas pode ser um conjunto de terminais montados de forma segura e ligados eletricamente ao invólucro do medidor, uma barra de ligação perto do invólucro do equipamento de serviço ou uma barra de ligação perto do elétrodo de terra. Esses terminais são especificamente para ligação e aterramento de comunicações e outros circuitos " intersistema ".
Se isto existir, o telefone e o prato devem ser ligados usando estes terminais.
800,100 (B) (2)
Se uma terminação de ligação entre sistemas não existir, esta seção fornece uma lista de alternativas aceitáveis. Incluído na lista está o " sistema de tubulação de água de metal interior ". Que pode ser usado desde que a conexão esteja dentro de 5 '(1,5 m) do ponto de entrada, e a tubulação esteja em contato direto com a terra por 10' (3 m) ou mais (250,52 (A) (1) ).
800,100 (B) (3)
Esta seção fornece ainda mais locais de ligação alternativos, e novamente aponta para 250,52 (A) (1) Tubo de água subterrânea de metal. .
tl; dr
A ligação ao sistema de tubulação de água pode não ser um problema, desde que a terminação esteja dentro dos primeiros 5 'do tubo que entra no edifício e o tubo esteja em contato direto com a terra por 10'. No entanto, se a união dielétrica não for condutora, deve haver um jumper de ligação de tamanho apropriado conectando as duas seções do tubo.
Se você estiver preocupado ou tiver problemas. Você poderia mover as terminações de ligação para o outro lado da união dielétrica, usar um método de ligação alternativo ou instalar uma terminação de ligação entre sistemas e usá-la.