O Código Elétrico Nacional requer a desconexão simultânea de condutores não aterrados de circuito de ramal multifilar.
NÃO requer disjuntores comuns.
Aqui estão os artigos pertinentes:
210.4(B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
Informational Note: See 240.15(B) for information on the use of single-pole circuit breakers as the disconnecting means.
240.15(B) Circuit Breaker as Overcurrent Device. Circuit breakers shall open all ungrounded conductors of the circuit both manually and automatically unless otherwise permitted in 240.15(B)(1), (B)(2), (B)(3), and (B)(4).
(1) Multiwire Branch Circuit. Individual single-pole circuit breakers, with identified handle ties, shall be permitted as the protection for each ungrounded conductor of multi-wire branch circuits that serve only single-phase line-to-neutral loads.
Observe que o último Artigo 240.15 (B) (1) permite que você use identificadores identificados em disjuntores de pólo único para circuitos ramificados de fios múltiplos.
Além disso, qualquer casa construída sob um código antigo (como 1983) é normalmente adquirida até que você faça grandes alterações, como substituir o painel, e tenha que atualizar para os novos requisitos de código.
Tanto quanto determinar quais circuitos são multifilares. Você pode começar com o branco e o preto nos disjuntores de 50 A que devem ser emparelhados. Então, qualquer fio vermelho estaria normalmente em um cabo multi-fio com um preto. Determinar qual vermelho combina com qual preto será seu projeto.
Boa sorte e fique seguro!