Ao determinar o tamanho do condutor do alimentador, você deve considerar a "
Embora o cabo / fio possa ser classificado em 90 ° C, você provavelmente descobrirá que os terminais são classificados em 75 ° C, ou não estão rotulados. 110.14 (C) (1) (a) nos diz que, já que estamos trabalhando com 100 amperes ou menos. Devemos usar a coluna de 60 ° C da Tabela 310.15 (B) (16) para determinar o tamanho do condutor, a menos que o equipamento esteja listado e rotulado para uma temperatura mais alta.
National Electrical Code 2014
ARTICLE 110 Requirements for Electrical Installations
110.14(C)(1) Equipment Provisions. The determination of termination provisions of equipment shall be based on 110.14(C)(1)(a) or (C)(1)(b). Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on Table 310.15(B)(16) (formerly 310.16) as appropriately modified by 310.15(B)(6).
(a) Termination provisions of equipment for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following:
(1) Conductors rated 60°C (140°F).
(2) Conductors with higher temperature ratings, provided the ampacity of such conductors is determined based on the 60°C (140°F) ampacity of the conductor size used.
(3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors.
(4) For motors marked with design letters B, C, or D, conductors having an insulation rating of 75°C (167°F) or higher shall be permitted to be used, provided the ampacity of such conductors does not exceed the 75°C (167°F) ampacity.
Como o cabo será executado a partir de um disjuntor no painel de serviço principal, para um disjuntor ou terminais em um subpainel. Temos que considerar a classificação de temperatura de ...
- Os condutores
- Os terminais no painel principal onde os condutores se conectarão.
- Os terminais no sub-painel onde os condutores se conectarão.
Usaremos então o menor valor, ou 60 ° C, se algum dos itens acima não estiver rotulado. Quando soubermos o tamanho dos dispositivos de sobrecorrente e a classificação de temperatura mais baixa, podemos usar a Tabela 310.15 (B) (16) para determinar o tamanho do condutor e o material que precisaremos.
Isso nos dará o tamanho atual do condutor necessário para o nosso alimentador.
Mas espere ...
Se você estiver trabalhando em uma unidade habitacional de uma, duas ou várias famílias, o Artigo 310.15 (B) (7) é aplicável?
National Electrical Code 2014
ARTICLE 310 Conductors for General Wiring
310.15 Ampacities for Conductors Rated 0–2000 Volts.
(B) Tables. Ampacities for conductors rated 0 to 2000 volts shall be as specified in the Allowable Ampacity Table 310.15(B)(16) through 310.15(B)(19), and Ampacity Table 310.15(B)(20) and Table 310.15(B)(21) as modified by (B)(1) through (B)(7).
The temperature correction and adjustment factors shall be permitted to be applied to the ampacity for the temperature rating of the conductor, provided the corrected and adjusted ampacity does not exceed the ampacity for the temperature rating of the termination in accordance with the provisions of 110.14(C).(7) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders.
(a) For individual dwelling units of one-family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(7), shall be permitted as 120/240-volt, single-phase service-entrance conductors and service lateral conductors.
NÃO.
Observe os códigos diz
"shall be permitted as 120/240-volt, single-phase service-entrance conductors and service lateral conductors".
Depois de ler a definição desses termos, fica claro que isso não se aplica à ligação entre o painel principal e um subpainel.
Service-Entrance Conductors, Overhead System. The service conductors between the terminals of the service equipment and a point usually outside the building, clear of building walls, where joined by tap or splice to the service drop or overhead service conductors.
Service-Entrance Conductors, Underground System. The service conductors between the terminals of the service equipment and the point of connection to the service lateral or underground service conductors.
Service Lateral. The underground conductors between the utility distribution system and the service point.
tl; dr
Condutores e todos os terminais com valor igual ou superior a 75 ° C.
Use 3 AWG de cobre ou 1 AWG de alumínio para os condutores de corrente.
Condutores com taxa igual ou superior a 75 ° C, terminais classificados a 60 ° C ou não rotulados.
Use 1 cobre de AWG ou alumínio de 1/0 AWG para os condutores de transporte de corrente.
Condutores e terminais classificados a 60 ° C.
Use 1 cobre de AWG ou alumínio de 1/0 AWG para os condutores de transporte de corrente.
Condutores classificados a 60 ° C, terminais com classificação superior a 60 ° C
Use 1 cobre de AWG ou alumínio de 1/0 AWG para os condutores de transporte de corrente.