De acordo com o Guia de instalação de fabricantes (PDF) ...
Physical - install the UTS within one foot of the building circuit breaker panel
<4>
Caution: The UTS must be installed within one foot of the building circuit breaker panel. If the UTS must be located further than one foot from the circuit breaker panel, a licensed electrician must extend the wiring using standard electrical wiring conduit and junction boxes.
De acordo com o National Electrical Code (NEC) ...
National Electrical Code 2011
ARTICLE 110 Requirements for Electrical Installations
110.3 Examination, Identification, Installation, and Use of Equipment.
(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
Eu estou supondo que a unidade tenha permanentemente conectado fios em uma pista, que é de um comprimento limitado. Portanto, montar a unidade mais longe do painel exigiria que você estendesse esses fios e pistas, o que requer o conhecimento dos métodos de fiação para fazer corretamente. Não é provável que você tenha que aumentar o tamanho dos fios, mas terá que entender os métodos básicos de fiação (Capítulo 1-4 da NEC).