Os kits de intertravamento do gerador são permitidos em aplicações residenciais?

8

Houve algumas perguntas no site recentemente, que usam kits de intertravamento com geradores portáteis.

Isso me inspirou a ler o artigo 702 Optional Standby Systems do NEC (que é curto, então não foi muito esforço), onde eu encontrei os seguintes itens que parecem relevantes.

NEC 2008
702.5 Capacity and Rating.
(B) System Capacity.
(1) Manual Transfer Equipment. Where manual transfer equipment is used, an optional standby system shall have adequate capacity and rating for the supply of all equipment intended to be operated at one time. The user of the optional standby system shall be permitted to select the load connected to the system.

Então, no caso de um intertravamento, o gerador teria que ser classificado para fornecer toda a casa, ou apenas os itens que o usuário deseja executar (o que poderia mudar a qualquer momento)?

702.6 Transfer Equipment. Transfer equipment shall be suitable for the intended use and designed and installed so as to prevent the inadvertent interconnection of normal and alternate sources of supply in any operation of the transfer equipment.

Um intertravamento instalado corretamente parece atender a esse requisito, então não há nada aqui para evitar um. No entanto, há uma exceção a essa seção que pode impedir o uso de intertravamentos em sistemas residenciais.

Exception: Temporary connection of a portable generator without transfer equipment shall be permitted where conditions of maintenance and supervision ensure that only qualified persons service the installation and where the normal supply is physically isolated by a lockable disconnecting means or by disconnection of the normal supply conductors.

Na minha opinião, esta frase " onde as condições de manutenção e supervisão garantem que apenas pessoas qualificadas atendem a instalação ". Significaria que um intertravamento não pode ser instalado em um painel residencial, porque não há como impedir que o proprietário faça manutenção na instalação.

Os intertravamentos são uma solução barata e fácil para os proprietários ou não podem ser usados em situações residenciais?

Atualizar

Eu encontrei esta resposta interessante em este tópico , no Fórum da Rede de Fornecedores de Energia Elétrica . Que parece ser de um representante de uma empresa que fabrica esses tipos de dispositivos.

O que basicamente diz que o dispositivo é compatível com NEC porque é o usuário que é o equipamento de transferência, não o dispositivo.

Eu também encontrei essa seção semi-relacionada, não relevante para a questão em questão, no NEC.

408.36 Overcurrent Protection.
(D) Back-Fed Devices. Plug-in-type overcurrent protection devices or plug-in type main lug assemblies that are backfed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.

O que significa que, se você estiver revertendo através de um disjuntor, você precisará prender o disjuntor no lugar de alguma forma.

    
por Tester101 07.01.2013 / 15:31

3 respostas

Parece que a decisão está finalmente nas mãos da Autoridade com Jurisdição (AHJ), contanto que " objetivos equivalentes possam ser alcançados " usando o dispositivo.

National Electrical Code 2008

ARTICLE 100 Definitions

Approved. Acceptable to the authority having jurisdiction.

Authority Having Jurisdiction (AHJ). An organization, office, or individual responsible for enforcing the requirements of a code or standard, or for approving equipment, materials, an installation, or a procedure.

ARTICLE 110 Requirements for Electrical Installations

110.2 Approval. The conductors and equipment required or permitted by this Code shall be acceptable only if approved.

ARTICLE 90 Introduction

90.4 Enforcement. This Code is intended to be suitable for mandatory application by governmental bodies that exercise legal jurisdiction over electrical installations, including signaling and communications systems, and for use by insurance inspectors. The authority having jurisdiction for enforcement of the Code has the responsibility for making interpretations of the rules, for deciding on the approval of equipment and materials, and for granting the special permission contemplated in a number of the rules.

By special permission, the authority having jurisdiction may waive specific requirements in this Code or permit alternative methods where it is assured that equivalent objectives can be achieved by establishing and maintaining effective safety.

This Code may require new products, constructions, or materials that may not yet be available at the time the Code is adopted. In such event, the authority having jurisdiction may permit the use of the products, constructions, or materials that comply with the most recent previous edition of this Code adopted by the jurisdiction.

AVISO

Embora esses dispositivos possam ou não ser aprovados pela AHJ, eles não são a melhor solução disponível. Eles não impedem que o usuário sobrecarregue o gerador, uma vez que a seleção da carga é feita pelo usuário dinamicamente durante a operação. A solução melhor e mais segura é instalar interruptores de transferência manuais ou automáticos. Isso permite que você pré-selecione as cargas, tornando-a uma solução mais amigável.

    
20.02.2013 / 18:33

Com base na citação:

Temporary connection of a portable generator without transfer equipment shall be permitted where conditions of maintenance and supervision ensure that only qualified persons service the installation and where the normal supply is physically isolated by a lockable disconnecting means or by disconnection of the normal supply conductors.

Não

Eu diria que qualquer proprietário de casa que não seja um eletricista licenciado NÃO poderá instalar um intertravamento. A única maneira segura de instalar um intertravamento temporário para um gerador portátil - digamos, no caso de falta de energia - é desconectar a rede elétrica principal da casa (mesmo que isso signifique desligar a rede principal).

Joe Average Homeowner não terá o treinamento necessário para manter esse fato de segurança em mente.

Além disso, como indicado nos comentários, Joe Average Homeowner pode remover facilmente a cobertura do painel, o que desabilitaria o intertravamento removendo-o, permitindo um cenário em que o comutador do gerador e o circuito principal possam ser acionados simultaneamente.

    
07.01.2013 / 15:59

Como um eletricista mestre, os kits de intertravamento são uma ótima opção e, se tiverem sido testados pela UL ou por outros grupos como o CSA, eles geralmente são aceitos pelos AHJs. Eu não iria comprar um barato, não testado, mas você pode comprá-los de OEM e obter o relatório de teste com o kit.

    
14.10.2013 / 22:04