Você pode querer verificar primeiro com o inspetor, mas vou dizer que eles permitirão. O NEC permite que o PVC seja suportado, passando por membros de enquadramento, portanto, suponho que eles permitirão que ele seja suportado quando estiver em execução em membros de enquadramento (especialmente em áreas inacessíveis).
National Electrical Code 2014
Chapter 3 Wiring and Protection
Article 352 Rigid Polyvinyl Chloride Conduit: Type PVC
352.30 Securing and Supporting. PVC conduit shall be installed as a complete system as provided in 300.18 and shall be fastened so that movement from thermal expansion or contraction is permitted. PVC conduit shall be securely fastened and supported in accordance with 352.30(A) and (B).
(B) Supports. ...Horizontal runs of PVC conduit supported by openings through framing members at intervals not exceeding those in Table 352.30 and securely fastened within 900 mm (3 ft) of termination points shall be permitted.