Desde que você está em uma residência de uma família, há realmente apenas um artigo importante para estar ciente.
800.26 Spread of Fire or Products of Combustion. Installations of communications cables and communications raceways in hollow spaces, vertical shafts, and ventilation or air-handling ducts shall be made so that the possible spread of fire or products of combustion will not be substantially increased. Openings around penetrations of communications cables and communications raceways through fire-resistant-rated walls, partitions, floors, or ceilings shall be firestopped using approved methods to maintain the fire resistance rating.
FPN: Directories of electrical construction materials published by qualified testing laboratories contain many listing installation restrictions necessary to maintain the fireresistive rating of assemblies where penetrations or openings are made. Building codes also contain restrictions on membrane penetrations on opposite sides of a fire resistance–rated wall assembly. An example is the 600 mm (24 in.) minimum horizontal separation that usually applies between boxes installed on opposite sides of the wall. Assistance in complying with 800.26 can be found in building codes, fire resistance directories, and product listings.
Em uma residência de uma ou duas famílias, você pode usar cabo de tipo geral (CM, CMG, CMX) em qualquer lugar que não seja onde o cabo de plenum é necessário.
800.154(B)(3) One- and Two-Family Dwellings. Type CM and CMX cable shall be permitted in one- and two-family dwellings.
Ou sob tapetes.
800.154(C)(6) Under Carpets. Type CMUC undercarpet communications wires and cables shall be permitted to be installed under carpet.