Você não pode colocar isso em uma nova estrutura de qualquer maneira
Enquanto a regra de seis (230,71) não é letra morta (ainda há casos em novas construções onde um painel sem disjuntor principal pode ser instalado), os painéis tipo "split bus" dos quais você fala não são mais Code , como violam 408.36, Exceção 1:
408.36 Overcurrent Protection. In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.
Exception No.1: Individual protection shall not be required for a panelboard used as service equipment with multiple disconnecting means in accordance with 230.71. In panelboards protected by three or more main circuit breakers or sets of fuses, the circuit breakers or sets of fuses shall not supply a second bus structure within the same panelboard assembly.
Mas, os painéis marinhos são animais totalmente diferentes
O equipamento elétrico marítimo é uma criatura diferente das coisas domésticas que você estava pensando inicialmente, e um pouco além do escopo deste site em alguns casos. Eu conversaria com um especialista familiarizado com os riscos sutis que a CA em um barco faz se eu estivesse em seus sapatos - os riscos de afogamento por choque elétrico são brutais .