I am putting new 100 amp service to my garage. Do I use only 100 amp meter socket or can I use a 125 amp

por Rob 22.02.2019 / 11:27

1 resposta

There is no reason why you cannot install a larger meter base than the one required. Keep in mind that equipment is rated to handle maximum currents not minimum. In your case a 100A meter base can only handle current up to 100A. Whereas a 125A handles up to 125A and will handle a 100A current without a problem.

Her's an idea. When I was working we always installed a 200A meter base since know you have the ability to upgrade a service if needed later, and comparing material cost the upgrade was minimal and labor is more or less the same. The only reason we would install a smaller base would be because of space restrictions.

Boa sorte