Ele deve ser protegido por GFCI e um receptáculo do tipo resistente às intempéries deve ser usado. Além disso, a tampa deve ser à prova de intempéries quando nada estiver conectado, embora eu recomende uma capa "em uso" ou "extra-duty".
Você não deve ter problemas para encontrar um receptáculo GFCI resistente às intempériese capas à prova de intempéries para esse estilo de receptáculo também são facilmente encontradas.
O artigo 210.8 (A) (3) do Código Elétrico Nacional estabelece que os receptáculos externos devem ser protegidos por GFCI.
National Electrical Code 2014
Chapter 2 Wiring and Protection
Article 210 Branch Circuits
210.8 Ground-fault Circuit-Interrupter Protection for Personnel.
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuit-interrupter protection for personnel.
(3) Outdoors
O artigo 406.9 (A) diz que os recipientes em locais úmidos devem ter tampas à prova de intempéries quando nada estiver conectado. Enquanto o 406.9 (B) (1), diz que os recipientes em locais úmidos devem ter tampas à prova de intempéries, mesmo quando algo estiver conectado. Ambas as seções também exigem que o receptáculo seja um receptáculo do tipo resistente a intempéries.
Chapter 4 Equipment for General Use
Article 406 Receptacles, Cord Connectors, and Attachment Plugs (Caps)
406.9 Receptacles in Damp and Wet Locations.
(A) Damp Locations. A receptacle installed outdoors in a location protected from weather or in a damp location shall have an enclosure for the receptacle that is weatherproof when the receptacle is covered (attachment plug cap not inserted and receptacle covers closed).
... All 15- and 20-ampere, 125- and 250-volt nonlocking receptacles shall be a listed weather-resistant type.
(B) Wet Locations.
(1) Receptacles of 15 and 20 Amperes in Wet Locations. Receptacles of 15 and 20 amperes, 125 and 250 volts installed in a wet location shall have an enclosure that is weatherproof whether or not the attachment plug cap is inserted. An outlet box hood installed for this purpose shall be listed and shall be identified as "extra-duty".
All 15- and 20-ampere, 125- and 250-volt nonlocking type receptacles shall be listed and so identified as the weather-resistant type.
Preferência pessoal aqui, mas eu gosto do tipo de "extra-duty" que cobre os acordeões quando em uso. Algo como o Hubbell-TayMac ML450G.
Como mantém um perfil mais fino quando não está em uso, mas oferece amplo espaço para rotear o cabo quando algo está conectado.