National Electrical Code diz que não.
National Electrical Code 2008
ARTICLE 210 Branch Circuits
210.52 Dwelling Unit Receptacle Outlets.
(B) Small Appliances.(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.
(3) Kitchen Receptacle Requirements. Receptacles installed in a kitchen to serve countertop surfaces shall be supplied by not fewer than two small-appliance branch circuits, either or both of which shall also be permitted to supply receptacle outlets in the same kitchen and in other rooms specified in 210.52(B)(1). Additional small-appliance branch circuits shall be permitted to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1). No small-appliance branch circuit shall serve more than one kitchen.
210,52 (B) (1) basicamente diz que todos os recipientes na cozinha devem ser fornecidos por 2 ou mais circuitos de 20A. 210,52 (B) (2) diz que não deve haver outras saídas nesses 2 ou mais circuitos, o que significa que não há saídas de iluminação e nem saídas fora da cozinha. 210.52 (B) (3) diz que os 2 ou mais circuitos, podem ser usados para fornecer receptáculos em outras salas ' relacionadas ' (despensa, sala de café da manhã, sala de jantar, ou área similar).
Mesmo que a cozinha e a sala de estar possam compartilhar uma parede; de acordo com a NEC 2008, eles não podem compartilhar um circuito elétrico.