Tudo bem, desde que você tenha um código novo o suficiente
A NEC de 2014 adicionou um novo ponto 4 em 250.130 (C):
(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates
(4) An equipment grounding conductor that is part of another branch circuit that originates from the enclosure where the branch circuit for the receptacle or branch circuit originates
(5) For grounded systems, the grounded service conductor within the service equipment enclosure
(6) For ungrounded systems, the grounding terminal bar within the service equipment enclosure
isso, junto com 250.134 (B) exceção 1:
Exception No. 1: As provided in 250.130(C), the equipment grounding conductor shall be permitted to be run separately from the circuit conductors.
permite fazer exatamente o que você está descrevendo (executando um fio terra separado em um ponto existente no sistema de aterramento do equipamento, originado no mesmo painel).
O fio mínimo necessário para isso é um fio 14AWG nu ou verde (THHN), mas eu usaria um cabo Bare Armored Ground (para deixar claro para futuros reformadores que isso não é algo que eles podem simplesmente cortar -normalmente). Você também precisará do cabo Bare Armored Ground se estiver exposto a danos físicos para atender aos requisitos de proteção de 250.120 (C).