NEC 2011 210.23 Permissible Loads. ... A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D)...
(A) 15- and 20-Ampere Branch Circuits: ...
(1) Cord-and-Plug-Connected Equipment Not Fastened in Place. The rating of anyone cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
O equipamento de utilização é qualquer coisa que se conecte à energia CA.
Você pode ter mais de um dispositivo instalado em um circuito, mas se eles somam > 50% da capacidade disponível, o circuito deve ser dedicado a eles. Nesse caso, um bom instalador instalará um único receptáculo (não duplex).
Se o aquecedor de água já estiver compartilhando um receptáculo duplex com sua carga de 12A, ele deverá ser
- inferior a 4 amps ou
- um MWBC. (circuito de ramal multi-fio, 2 hots compartilhando um neutro).
O mais provável é que o fabricante tenha escolhido 12A porque 125% disso é 15A, o que o torna o tamanho perfeito para um circuito de 15A. 125% porque carga contínua. Não que eu aspire por + 3 horas de cada vez!