Use a regra de 80% para cargas contínuas (porque o disjuntor, mesmo que você não o faça)
Embora o 210.22 pareça indicar que você tem os 30A completos disponíveis para você:
210.22 Permissible Loads, Individual Branch Circuits. An individual branch circuit shall be permitted to supply any load for which it is rated, but in no case shall the load exceed the branch-circuit ampere rating.
você tem que considerar que o disjuntor pode ter outras idéias, como indicado em 210.20 (A):
(A) Continuous and Noncontinuous Loads. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load.
Exception: Where the assembly, including the overcurrent devices protecting the branch circuit(s), is listed for operation at 100 percent of its rating, the ampere rating of the overcurrent device shall be permitted to be not less than the sum of the continuous load plus the noncontinuous load.
A razão é porque os disjuntores de jardim feitos para UL 489 (e suas contrapartes em terra de fusível) irão eventualmente desarmar (ou explodir) se você executar 100% de sua corrente nominal através deles por horas a fio. Embora exista algo como um separador de 100%, eles são normalmente encontrados apenas em trabalhos industriais.
Além disso, a fiação do circuito de ramificação também precisa de uma redução de 80% para cargas contínuas, conforme 210.19 (A) (1):
(1) General. Branch-circuit conductors shall have an ampacity not less than the maximum load to be served. Conductors shall be sized to carry not less than the larger of 210.19(A)(1)(a) or (b).
(a) Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.
(b) The minimum branch-circuit conductor size shall have an allowable ampacity not less than the maximum load to be served after the application of any adjustment or correction factors.
Exception: If the assembly, including the overcurrent devices protecting the branch circuit(s), is listed for operation at 100 percent of its rating, the allowable ampacity of the branch-circuit conductors shall be permitted to be not less than the sum of the continuous load plus the noncontinuous load.
Portanto, você está limitado a 5760W por um tempo de permanência no mesmo local (ou pelo menos mais de algumas horas por vez). Cargas não contínuas (digamos, um motor de bomba de poço grande), no entanto, podem puxar 7200 W do circuito, já que o ciclo de trabalho da carga fornece tempo suficiente para que as coisas se acalmem entre as operações.