De fato, fornecido o assembly é listado pelo UL para o propósito , não há problemas de código envolvidos. As passagens aplicáveis são 210.52 (C) (5) (ênfase minha):
(5) Receptacle Outlet Location. Receptacle outlets shall
be located on or above, but not more than 500 mm (20 in.)
above, the countertop. Receptacle outlet assemblies listed
for the application shall be permitted to be installed in
countertops. Receptacle outlets rendered not readily accessible by appliances fastened in place, appliance garages,
sinks, or rangetops as covered in 210.52(C)(1), Exception,
or appliances occupying dedicated space shall not be considered as these required outlets.
e 406,5 (E):
(E) Receptacles in Countertops and Similar Work Surfaces. Receptacles, unless listed as receptacle assemblies
for countertop applications, shall not be installed in a
face-up position in countertops or similar work surfaces.
Where receptacle assemblies for countertop applications
are required to provide ground-fault circuit-interrupter protection for personnel in accordance with 210.8, such assemblies shall be permitted to be listed as GFCI receptacle
assemblies for countertop applications.
Infelizmente, o T & B KPR-15G está em "permanente engenharia", não me pergunte por que - caso contrário, parece ser o melhor exemplo de tal montagem. Se você não se importar com a diferença na aparência, no entanto, você pode usar a série Lew PUFP (eles aparecem em um "ângulo lateral" versus o pop-up vertical nas unidades T & B e Mockett, como mostrado em
este PDF ). Infelizmente, a imagem na pergunta retrata a versão Mockett deste conceito, que é
suspiro listado como um toque de energia portátil e, portanto, não é compatível com código neste aplicativo.